Re: Question over old outlets

Unclean canine: 1975 NEC section 210-7, was the first year that all 15 and 20 amp receptacles in residential occupancies, were required to be the grounding type.
 
Re: Question over old outlets

Cool! Thanx. For some reason I was thinking it was 1972 but wasn't sure.

Now, here's another old outlet question...

In the older homes I've noticed two types of 120 volt outlets used. One type just has the vertical slots. Then there's another type, which I believe is referred to as a "combination 15 amp/20 amp outlet." It has the vertical slots as well but in addition to that it has horizontal slots that "tee" into the vertical slots. Both the hot and the neutral sides of this outlet have the extra slots cut into it.

I was curious when the first and last years of this "combination" outlet was used? Seems like most homes I've seen built in the mid 50's to late 60's had them?

Thanx again.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Question over old outlets

Thanks, that answered my first question.
Now:
1. When was NM cable first allowed in the NEC?
2. The first NM w/ ground cable used a reduced size equipment grounding conductor, wasn't it 14 AWG for 12-2 NM? What year was NM cable introduced with the reduced size equipment grounding conductor (if I am correct on that)?
 

tonyi

Senior Member
Re: Question over old outlets

The first nasty 2-wire NM showed up sometime around 1920 I believe.

That undersized gnd was also used on #10 - I just rewired a 30A dryer some dope used that stuff on (and they used a 10-2. Insulated neutral?!?). It looked like the gnd was about #14. on the #12's that gnd isn't even a #14, more like a #16, its real flimsy. If a breaker failed and you wound up having to trip the main on a fault, things could get pretty toasty pretty quick :p
 

earlydean

Senior Member
Re: Question over old outlets

I recall when I first started electrical work in 1970, there were NM cables with the reduced size grounds. I did commercial projects for a number of years. Later, in 1975, when I wired a few homes with NM, the grounds were full size.
 

dana1028

Senior Member
Re: Question over old outlets

RE: undersized EGC in NM cable...I'm wondering if that was a UL thing. Up through 1984 the NEC said (regarding EGC in NM)..."In addition to the insulated conductors, the cable may have an approved size of insulated or bare conductor for equipment grounding purposes only."

In 1987 this changed to require this EGC to be sized according to Art. 250 ("when provided, the grounding conductor shall be sized in accordance with Art. 250)...Table 250-95 (Min. Size EGC) required full sized conductors for 15-, 20- and 30-amp circuits.
 

dana1028

Senior Member
Re: Question over old outlets

dirty dawg - those receptacles you are referring to were 15A, 125v OR 10A, 250v receptacles. I have a very clear photo of one of those, just don't know how to attach it here.

bryant.jpg


The photo link was provided through the consideration of Wayne C. (awwt).

You can see that this innocent looking 15A (2-prong) receptacle could actually be wired up for 240v !!! what a surprise for someone!

[ November 17, 2003, 07:48 PM: Message edited by: dana1028 ]
 
G

Guest

Guest
Re: Question over old outlets

Wouldn't it be 20amp 125 volt?

16352photo.jpg
 
Re: Question over old outlets

Wayne, it looks like the outlet you've posted a pic of, except it has that horizontal slot that you see on the neutral side as well as the hot side, plus it does not have the ground hole.

Seems like most of the houses I've seen them in were built in the later 50's into the 60's. I was curious on the years they were actually used.

I have a pic somewhere if I can find it...


Thanx.

[ November 17, 2003, 05:54 PM: Message edited by: dirty dawg ]
 

hurk27

Senior Member
Re: Question over old outlets

The photo that Dana posted are no longer allowed as the NEC says that they can't be interchangable.

406.7 Noninterchangeability.
Receptacles, cord connectors, and attachment plugs shall be constructed so that receptacle or cord connectors do not accept an attachment plug with a different voltage or current rating from that for which the device is intended. However, a 20-ampere T-slot receptacle or cord connector shall be permitted to accept a 15-ampere attachment plug of the same voltage rating. Non?grounding-type receptacles and connectors shall not accept grounding-type attachment plugs.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Question over old outlets

Hurk, you are correct. Here is another picture of this receptacle. This one is a porcelain version Hubbell model # P-749

Mvc-015f.jpg


Roger
 

dana1028

Senior Member
Re: Question over old outlets

It looks like 1975 is when the code changed; i.e. it added code sections prohibiting the interchangeable types of receptacles. 210-7(f) and 410-56(e) were added.
 

tonyi

Senior Member
Re: Question over old outlets

Maybe dancing visions of potential european sales during the post-war reconstruction era. A universal unit that would work either side of the pond. We weren't going to get'em off 220V, but with all the US bucks flowing in maybe we could get'em to use our plugs...

Yea right.
 
Re: Question over old outlets

Originally posted by dana1028:
dirty dawg - those receptacles you are referring to were 15A, 125v OR 10A, 250v receptacles.

bryant.jpg


The photo link was provided through the consideration of Wayne C. (awwt).

You can see that this innocent looking 15A (2-prong) receptacle could actually be wired up for 240v !!! what a surprise for someone!
Thanx....yes that is it....that is a definite pic of the outlet I'm referring to! But of course I had a guy tell me it was a "combination 15 amp/20 amp outlet." And in a way it seems to make sense since I've noticed on a 20 amp plug one blade is vertical and the other is horizontal.

But now if that outlet could be used for 240 volts, was it most likely in another country? Because most of the 240 volt outlets I've seen here in the US (I believe) are made up of two 120 volt lines, then the neutral (and sometimes a ground). Over in Europe and other middle eastern countries I believe it's only one 240 line and then a neutral. (That's correct isn't it it?)

And since it's sort of a "universal" outlet, I take it that's why they're not made anymore? Because they still sell the standard type vertical slot non grounded outlets at Lowes and other home supply stores but they don't sell these.

Tonyi, in your post, were you referring to that these outlets began being produced after WWII? (Just curious)

Thanx.

[ November 18, 2003, 01:47 AM: Message edited by: dirty dawg ]
 

tonyi

Senior Member
Re: Question over old outlets

The real early stuff is typically a non-polarized ordinary 2-prong (virtually worthless these days). Most places I've seen this variety seemed to be post WWII vintage wiring. Nothing hard and fast to go by of course.
 
Re: Question over old outlets

I don't think I've ever saw a non polarized 2 prong duplex outlet....with the exception of the pic of the one that has it's face removed from the rest of it....aka the "porcelain outlet."

Seems like most of the homes I've seen those "t-slot" outlets in were built in the 50's and 60's so that's why I was thinking you meant maybe they were made after WWII....but not all homes have them. The house I grew up in was built in 1948. Out of all of the outlets it had only three that I remember were the t slot type and the rest were the standard 2 prong duplex outlets. My grandfather's house was built in the early 60's and it had those t slot ones in every room of the house except the kitchen and the garage.....they were grounded 20 amp type.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Question over old outlets

Actually the porcelain receptacle is polarized, it's just hard to see it in the picture.

Roger
 