Question parallel conductors

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 6-#3 awg conductors plus #6awg gnd between fire pump controller and fire pump that is 40HP, 208V three phase.

I did research minimum size parallel allowed is #1/0 awg and ampacity derating apply for more than 3 current carrying conductors.

However, I am not able to find this:
Can you parallel in one conduit two sets of #3 awg or not?
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
You cannot parallel #3 AWG condcutors but you did say a fire pump and many fire pumps are Wye start/Delta run so there are 6 conductors between the controller and the fire pump.

So then it may not be paralleled? I dont follow


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So then it may not be paralleled? I dont follow
Are you familiar with Wye start/Delta run motors? They have 6 conductors from the controller to the motor. You need to confirm the type of fire pump controller that you have. If it's Why start/Delta run the conductors are not normal parallel conductors which are required to be #1/0 and larger.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
To expand on Rob's last post, the six conductors of a wye start delta run do not carry current at the same time. Three will be energized at start up and drop out after the motor has reached a running state where the other three will take over.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
To expand on Rob's last post, the six conductors of a wye start delta run do not carry current at the same time. Three will be energized at start up and drop out after the motor has reached a running state where the other three will take over.
I don't understand.
The six conductors are the two ends of each of the 3 windings. In the wye start, one end of each winding is connected to the power source and the other ends are shorted together at the stater to create a wye connection.
For the delta run, each end of each coil is connected to the power source to create a delta connection.
In both cases, all six conductors carry current.
1710350707304.jpeg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
In both cases, all six conductors carry current.
That's correct. Wye start/Delta run conductors are sized at 72% (58*125%) of the running motor current for that reason. All six carry current it's the configuration that changes through the starter.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I don't understand.
The six conductors are the two ends of each of the 3 windings. In the wye start, one end of each winding is connected to the power source and the other ends are shorted together at the stater to create a wye connection.
For the delta run, each end of each coil is connected to the power source to create a delta connection.
In both cases, all six conductors carry current.
View attachment 2570539
You are correct, I should have said "full load current"
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
In both cases, all six conductors carry current.
Thanks for the explanation. The above would matter for ampacity adjustment.

But for the OP's question, the point is that in neither case are the load end of any two conductors directly connected together, so never do you have two conductors in parallel in the 310.10(G) sense.

Cheers, Wayne
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Thanks for the explanation. The above would matter for ampacity adjustment.

But for the OP's question, the point is that in neither case are the load end of any two conductors directly connected together, so never do you have two conductors in parallel in the 310.10(G) sense.

Cheers, Wayne
I think that's the "clue". With the wye/delta they are not parallel conductors.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Fire pump Controller is wye delta.

If they are not inparallel then My only question now is full load amps is 115A.

For fire pump supply conductors should it not be 115x1.25=143.75A which should be minimum #1/0 awg each instead of #3 awg?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Fire pump Controller is wye delta.

If they are not inparallel then My only question now is full load amps is 115A.

For fire pump supply conductors should it not be 115x1.25=143.75A which should be minimum #1/0 awg each instead of #3 awg?
So, the FLA is based on a 3-wire delta-connected load. If you look at the diagram in post 7, where there are blue dots at the end of each coil, a single wire would be connected to both blue dots at each corner of the triangle of coils. That wire would be carrying current from each of the two coils connected to that point (if you like, the "outbound" current from one coil and the "return current" from the other), and those two currents are 60 degrees out of phase with each other. That means the wire is carrying sqrt(3) * the coil current (not twice, due to the phase difference).

In other words, the coil current in 1/sqrt(3) times the FLA. And with 6 conductors going to the motor, in the delta configuration each wire is only carrying a single coil current, there's no combining currents as in a 3-wire delta connection. So each wire would see 115A / sqrt(3) = 66A at full load, and after the 125% factor, that gives 83A. Thus the required ampacity is only 83A (didn't actually check that the appropriate section of Article 430 specifies this, but it must). This is what infinity was alluding to in post #8, 1/sqrt(3) = 58%.

Cheers, Wayne
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
So, the FLA is based on a 3-wire delta-connected load. If you look at the diagram in post 7, where there are blue dots at the end of each coil, a single wire would be connected to both blue dots at each corner of the triangle of coils. That wire would be carrying current from each of the two coils connected to that point (if you like, the "outbound" current from one coil and the "return current" from the other), and those two currents are 60 degrees out of phase with each other. That means the wire is carrying sqrt(3) * the coil current (not twice, due to the phase difference).

In other words, the coil current in 1/sqrt(3) times the FLA. And with 6 conductors going to the motor, in the delta configuration each wire is only carrying a single coil current, there's no combining currents as in a 3-wire delta connection. So each wire would see 115A / sqrt(3) = 66A at full load, and after the 125% factor, that gives 83A. Thus the required ampacity is only 83A (didn't actually check that the appropriate section of Article 430 specifies this, but it must). This is what infinity was alluding to in post #8, 1/sqrt(3) = 58%.

Cheers, Wayne

NEC 2017 Article 430.22(C) is the correct section then for sizing conductors for this type of controller?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
NEC 2017 Article 430.22(C) is the correct section then for sizing conductors for this type of controller?
Yes if it's Wye start Delta run those are the values you use. 58%*FLC*125%=FLC*72%.
If they are not inparallel then My only question now is full load amps is 115A.

For fire pump supply conductors should it not be 115x1.25=143.75A which should be minimum #1/0 awg each instead of #3 awg?
No #1/0 is not required because you're spreading the load across 6 conductors not 3.
 