hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 6-#3 awg conductors plus #6awg gnd between fire pump controller and fire pump that is 40HP, 208V three phase.
I did research minimum size parallel allowed is #1/0 awg and ampacity derating apply for more than 3 current carrying conductors.
However, I am not able to find this:
Can you parallel in one conduit two sets of #3 awg or not?
I did research minimum size parallel allowed is #1/0 awg and ampacity derating apply for more than 3 current carrying conductors.
However, I am not able to find this:
Can you parallel in one conduit two sets of #3 awg or not?