I have a Question pertaining to Article 680-10

No lectures please,I Know this should not have happen but it did.

My question is this , what would you do if by accident a feeder conduit got Installed with in 3-4 feet from an in ground pool that's NOT related to Pool Equipment and was Inspected and now buried - 5 feet deep.

I found this article some where on this forum but I am still unclear of the wording.

I wont post the article - 680.10 - but the understanding from another forum member.

Thanks in Advance
WinZip



The first sentence in this article states that NO underground

wiring is permitted within 1.5 m (5 ft) from the inside wall of the pool unless it

is necessary to supply pool equipment. The next sentence needs clarification, as

it is being interpreted that ANY underground wiring (even if it is not necessary

to supply the pool equipment) is permitted within the 1.5 m (5 ft) area so long

as it is installed in an approved raceway at the depths listed in the chart. By

adding the phrase that is necessary to supply the pool equipment to this second

sentence (where I indicated above), it clarifies the intent of the article.



Panel Meeting Action: Reject



Panel Statement: The intent of the Code is to permit, when space is limited,

conduits from other systems to be buried within 5 ft of the pool in accordance

with 680.10 and Table 680.10.



The second sentence clearly creates an exception to the first. I agree that the first sentence should have included the word "except" in some fashion. But the meaning is not ambiguous. You can do it under the circumstances described in the second sentence, but not otherwise.
 
Welcome to the forum.:)

What type of wiring method is the feeder run in?

Table 680.10 gives you some relief from the 5' distance provided that you use one of the raceways listed in the table.

Chris
 
It's in sch 40 pvc and it's a concrete pool.

Provided that space limitations prevented this feeder from being installed at least 5' feet from the wall of the pool, Table 680.10 would permit the feeder to be located less than 5' provided that the PVC was a complete system and buried at least 18" deep.

Chris
 
The feeder conduit was placed to close to the pool by mistake an the Electrical Inspector either missed it or did not see it and passed the Inspection an shortly after this IDIOT crew came in a buried everything before we could relocate it . now I don't know what to do maybe re run the whole run 140 feet - It just baffles me with people any more