When verifying existing loads on an existing feeder for the addition of new loads per 220.87 can the 30-day continuous recording requirement be accomplished by daily spot checking of existing meter displays over a 30-day period? To me the word "continuous" would not allow that and would require a continuous recording?
Also when trying to measure the total load on existing SWBD if it is not practical to monitor main on SWBD can the monitoring process happen by setting up (3) meters on outgoing feeders from SWBD and adding the cumulative currents (same time stamp) to arrive at the total current? Depending on power factor of loads on each feeders wouldn't the current angles for each feeder be different and not follow linear addition (would require phasor addition)?
Also when trying to measure the total load on existing SWBD if it is not practical to monitor main on SWBD can the monitoring process happen by setting up (3) meters on outgoing feeders from SWBD and adding the cumulative currents (same time stamp) to arrive at the total current? Depending on power factor of loads on each feeders wouldn't the current angles for each feeder be different and not follow linear addition (would require phasor addition)?