A switchboard close by feeds a main-lug only (No Main) panel. Can this panel have more than 6 breakers or it has to have a main breaker according to article 225.33 (A)?
It is next to it. What determines a Detach structure? Is there a distance limit?
Is there OCP on the feeder that feeds the panel?A switchboard close by feeds a main-lug only (No Main) panel. Can this panel have more than 6 breakers or it has to have a main breaker according to article 225.33 (A)?
Is there OCP on the feeder that feeds the panel?
But are they in the same structure?Yes, there is OCP on the feeder panel.
there is no minimum distance. Do the structures share common structural members such as framing, a roof, or similar? If not, it is a separate/detached building.
Then IMO you are not limited to six throws because there is a single throw upstream of it.Yes, there is OCP on the feeder panel.
To iterate what you said if the panels are in the same building but different rooms, article 225.33(A) does not apply. If the panels are outside but on different equipment pad, article 225.33 (A) applies.
Please advise.