rickcola813
Member
- Location
- New York City
- Occupation
- Project Manager
I built a simple spreadsheet to help me assess conduit fill. I just ran into a conflict with an engineer. They are asking for us to pull 3 @ #2 AWG THHN conductors into 1" EMT. My spreadsheet shows that 3 @ #2AWG THHN conductors have a combined CMA of .3472 cubic inches. The spreadsheet also shows that the cross sectional area of 1" EMT is .864". When .3472 is divided into .864 I get 40.2%; which is greater than the 40% required. Am I calculating incorrectly or is it acceptable to round the answer up or down to the nearest number therefore making 40.2% acceptable?