The "Six Hand Rule" regarding service disconnects is all about firefighters not having to move their hand more than 6 times to kill all power in a building. That then ostensibly means the firefighters enter the service disconnect area, be it inside a room or not, to kill power that way. That of course is our ELECTRICAL code, the Fire Marshal for any given area may / will have their own SOP.
Side note to that, I got involved a few years ago in an issue here in California when solar started to take off, because firefighters were killing power to a building, then getting shocked by the solar system when chopping into a roof because it was still making electricity even though it didn't go anywhere. So the local Fire Marshall's group started insisting that solar panels had disconnects on the outside, or else some other way of killing power from the panels. Since the panels were DC, the disconnects had to be rated for that (not all are, especially above 250VDC). But homeowners with "solar roofs" (integrated solar cells in shingles) complained about having ugly gray boxes with red handles ruining their esthetics. I was contacted by a big solar roof supplier. We designed a 600VDC contactor system that went UNDER the roof and was controlled by the house power. So when they killed the Main, it dropped out the control power to the contactor coils and killed the DC coming out of the panels. Sold about 100k of those, now they do it differently (but I'm not longer in that world).