gary b said:
A question came up in class I cannot answer. Will you explain why metal frame of a building and concrete encased electrodes, both suitable as ?stand alone? electrodes, are no longer allowed as augmented electrodes in 250.56 but are allowed for a supplemental electrode for metal water pipes in 250.53(C)(2)?
250-50 allows us to use a CCE (ufer) all by itself as well as all the other electrodes, but a water pipe electrode MUST BE supplemented regardless of ohms 250-53(D). This is due to the fact a non-skilled individual can alter it causing rendering it disabled. In my opinion the author intentionally convolutes the wording in 250-50.
The '05' Handbook gives a good explanation about 250-50, Grounding electrode system, 'the NEC encourages the formation of a system of electrodes" i.e. more than one. The Ufer is worthy of stand-alone but so are the others especially if they read low ohms, if in doubt install additional electrodes and form a system. I personally wouldn't bother because often I don't believe its necessary.
Grounding has a purpose and is important when used but bonding is far more critical and important. The likelihood of ever being used proves this; think about the purpose of grounding 250-(4)(A)(1):
?
Lightning - could happen but the flash will travel multiple ways regardless of low ohms through electrodes to earth these may just get the majority of the voltage. If lightning is great concern install a designed lightning rod system.
?
Line surges - could happen with upstream powerhouse problems or transformer failure but stuff is going to have to blow up or arc before an electrode will be used. A relay can be installed to shunt the main to circumvent this problem.
?
Unintentional contact with higher-voltage lines - could happen and the downstream voltage will increase proportionally but again stuff is going to have to blow up or arc before an electrode will be used. And relays can be installed to shunt the main.
In premises wiring grounding to earth has nothing to do with how circuits function, bonding functions, ground fault functions, or neutrals function but bonding does!
Bonding is what enables 250-4(A)(4) & (5)
effective ground fault current path. Without this fault path breakers will not trip and electrocution is
highly likely. Because of the likelihood of use the bonding deserves more emphasis than grounding to earth.