hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have two buildings same owner. First building is 13,888 square feet is Fire Station Building and second building 14,280 square feet is Training Facility Building accessory to the Fire Station building.
I have incoming electric utility first building into service disconnect whose load side feed MDP. The MDP in first building has 200A feeder breaker feeding the second building Panel CP power and light. Panel CP equipment grounding bus is connected to GES but has no main bonding jumper.
Inspector comes along and says you cannot feed second building with feeder breaker and is a violation of NEC 2014 Article 230.2 building shall be served with only one utility service.
I point to NEC 2014 Article 225.30 which says building served by feeder but he just reitrated second building has to be served by utility NEC 2014 Article 230.2.
Is the inspector correct?
Thank you for all your input
I have incoming electric utility first building into service disconnect whose load side feed MDP. The MDP in first building has 200A feeder breaker feeding the second building Panel CP power and light. Panel CP equipment grounding bus is connected to GES but has no main bonding jumper.
Inspector comes along and says you cannot feed second building with feeder breaker and is a violation of NEC 2014 Article 230.2 building shall be served with only one utility service.
I point to NEC 2014 Article 225.30 which says building served by feeder but he just reitrated second building has to be served by utility NEC 2014 Article 230.2.
Is the inspector correct?
Thank you for all your input