The definition of feeder includes conductors from a separately derived system.
I am going to apply the outside feeder tap rule and I am not going use an OCPD at the generator, even if the generator is supplied with built in OCPD.
Since I am not using the OCPD at the generator, I will install the system bonding jumper at the 600 amp disconnect.
Not sure what you mean by "reground" as my understanding of that term is a second connection between the neutral and the earth which is not permitted.
If you would use the OCPD at the generator, then you would install the system bonding jumper at that point, and have to provide a grounding electrode system at the generator and connect the GEC at the generator. You would then run 3 ungrounded conductors, a grounded conductor, and equipment grounding conductor to the 600 amp disconnect. At that point you would connect the EGC to be building grounding electrode system and run the 3 ungrounded conductors, a grounded conductor, and equipment grounding conductor to the switch gear. Just not how I would make this installation, but that would also be code compliant.