Existing residential installation circa 1960s
Fused Service disconnect (150 amp) adjacent to meter with 3 conductor cable feeding across the house to what used to be the service and is now a sub-panel w/ no main equipment grounding conductor and with circuit neutrals and equip grounds on same neutral bar.
Would it be compliant to simply run a #6 EGC along side the existing 3 conductor feeder from the disconnect to the sub-panel?
 
Existing residential installation circa 1960s
Fused Service disconnect (150 amp) adjacent to meter with 3 conductor cable feeding across the house to what used to be the service and is now a sub-panel w/ no main equipment grounding conductor and with circuit neutrals and equip grounds on same neutral bar.
Would it be compliant to simply run a #6 EGC along side the existing 3 conductor feeder from the disconnect to the sub-panel?
Kind of not, but I would rather see that then no EGC in most instances. Other question is what kind of three wire cable?
 
It was an old cloth covered type cable with 3 conductors of #1 or 1/0 cu RBW. I haven't seen that type cable before. It may have been an early type of SER similar to the old 2 wire with braid service cable in "60s houses or maybe just a large size of the early non-metallic cable w/o ground.
 
It was an old cloth covered type cable with 3 conductors of #1 or 1/0 cu RBW. I haven't seen that type cable before. It may have been an early type of SER similar to the old 2 wire with braid service cable in "60s houses or maybe just a large size of the early non-metallic cable w/o ground.
Was the neutral insulated was one of my main concerns for asking?
 
Yes....3 insulated conductors. Isn't there something in the NEC regarding all conductors of a circuit or feeder being in the same raceway or cable assembly? And would that apply to the EGC as in this situation?
 
Yes....3 insulated conductors. Isn't there something in the NEC regarding all conductors of a circuit or feeder being in the same raceway or cable assembly? And would that apply to the EGC as in this situation?
Yes, 110.54(B) [2011], but with specific exceptions for branch circuits which did not have an EGC originally, 250.130(C). A new EGC for an old circuit is allowed several specific alternates to running a wire or raceway back to the panel. Some of them, by their nature, could not run in same raceway or cable without rewiring, so there is presumption that a separated wire is allowed.
 