Hi, Mike. I have a couple quick questions on installing a 15kVA transformer with wire-type leads. It’s fed from a 480 volt primary with secondary’s feeding a 120/240 volt panel. The primaries consist of (2) #8 THHN’s and a #10 THHN ground protected by a 2-pole 40 amp breaker. My boss told me that I don’t need a ground rod at the transformer, just to land the #10 on the lug provided. Doesn’t it need a GEC and bonded? He also told me to run #4 THHN’s to a 100 amp panel saying they are protected by the primary OCPD. Don’t the ampacity of the secondary conductors have to equal the rating of the panel board? I am very interested to hear your thoughts. Thanks! Matthew Schmidgall