First some background information. The panelboard in question is designed with the following specifications by the manufacturer:
Type: CDP
Amps: 100
Date: 6/85
Series: 8A
Voltage: 208Y/120V
System: 3 Phase, 4 Wire
Manufacturer: I-T-E Panelboards (S.O. 18 95114)
The problem that I have observed, along with some other electricians, is that the inner panel cover
that conceals the breakers has been intentionally cut (maybe by a "SAWZALL") in order to accomodate three additional 20 AMP breakers. To clarify, the panel appears to be designed only to allow 30 OCPD's and one MAIN 3 POLE OCPD rated for 100 AMPS in this installation; however, and this is conjecture on my part, I would submit that whoever made this modification was probably trying to add three more circuits, maybe multiwire branch, and was to cheap or ignorant to carry out the installation according to proper N.E.C. rules.
Nevertheless, the questions to be answered are:
Is this modification considered to be a flagrant violation of the National Electrical Code?
If not, then could it be a violation of the manufacturer's intended use of the panelboard especially when there were no twist out filler plates left to be removed? (NOTE: All 30 single pole slots were filled not including the 3 slots at the bottom right used for the 3 pole MAIN Breaker)
If there is a violation here, then what article section or sections can I or we reference to clear up this dilemma?
Any input from the members of the forum is appreciated. Thank you for time.
Type: CDP
Amps: 100
Date: 6/85
Series: 8A
Voltage: 208Y/120V
System: 3 Phase, 4 Wire
Manufacturer: I-T-E Panelboards (S.O. 18 95114)
The problem that I have observed, along with some other electricians, is that the inner panel cover
that conceals the breakers has been intentionally cut (maybe by a "SAWZALL") in order to accomodate three additional 20 AMP breakers. To clarify, the panel appears to be designed only to allow 30 OCPD's and one MAIN 3 POLE OCPD rated for 100 AMPS in this installation; however, and this is conjecture on my part, I would submit that whoever made this modification was probably trying to add three more circuits, maybe multiwire branch, and was to cheap or ignorant to carry out the installation according to proper N.E.C. rules.
Nevertheless, the questions to be answered are:
Is this modification considered to be a flagrant violation of the National Electrical Code?
If not, then could it be a violation of the manufacturer's intended use of the panelboard especially when there were no twist out filler plates left to be removed? (NOTE: All 30 single pole slots were filled not including the 3 slots at the bottom right used for the 3 pole MAIN Breaker)
If there is a violation here, then what article section or sections can I or we reference to clear up this dilemma?
Any input from the members of the forum is appreciated. Thank you for time.