I have a situation where the engineer is proposing an installtion that I don't believe is code compliant. Please review the situation below and tell me if I'm off base.
I have one 1600 AMP disconnect that is going to feed two 1200 AMP MB panels. The feeds for each panel contain 1200 amps worth of conductors. The distances of the feeds are 40' and 150'.
IMO this greatly exceeds the distances permitted by the NEC "tap" rules, therefore the feeders must be protected at 1200 amps each by replacing the 1600 amp disconnect with (2) 1200 amp OCD's. Am I all wet? The 2005 NEC does applies to this situation.
I have questioned the engineer on this and he tells me that it is compliant.
Thanks for your input.