When given the square footage of a residence and that there is a bathroom and laundry circuit being the only information given, it seems to me that the only code requires that 3000VA be included in the calculations. But what else? If a particular load is not specified, it seems to me that indicates electrical power provisions for such appliances don't need to be included in the calculations for reasons that the appliances may be gas. It seems to me that gas appliance power needs and the bathroom circuits are included in the general lighting calculation of 3va /sq feet according to my understanding of the NEC. To calculate electrical appliance loads like a range, oven, dryer, window air conditioner, electric furnace, the nameplate rating is required. Therefore, if the square footage of this residence if 1000 sq feet, garage not included, would have a general lighting load of 3000, 1500 for the washer, and 3000 for the two require kitchen small appliance circuits. The total demand factor would be 3000 at 100%, and the remaining 4500 at 35% or 1575 va for a total demand factor of 4575 va. Please correct me if I am wrong.