I seem to have lost a neutral somewhere as after hooking up the ballast and getting readings I'm getting 108v on the common tap going in and 115 on the 208v tap. 15 volts between them. My first step tomorrow will be to disconnect power at the bottom of pole and check voltages but what do these symptoms point to. It's 208v with no neutral in the light just 2 legs.
Im a little confused by your description. Its unlikely you would see symptoms of a lost neutral on only one pole light branch circuit. Especially a 208v one.
Which wires are you testing voltage on?
You should have two power wires and a ground coming to the top of the pole. Those power wires should read 208 across them on your meter. Are these the wires you're testing?
If so, and you are getting strange voltages, than i think its like auggie said about a bad contact on the contactor. You said you have 4 contactors so there's a decent chance each pole could be fed individually. When you turn the power on tomorrow morning, take a few minutes to check the line and load side of every contact on all the contactors.
If you're checking for voltage THROUGH the ballast, BE CAREFUL. You should expect to see strange voltages if you're checking wires coming from the ballast transformer. This scenario would make me think you have just miswired the ballast kit. What type of lamp is the ballast for?
Im not a stickler for safety, but i probably wouldn't let you test a live circuit with a meter in a bucket truck just yet. I Don't mean that as a personal attack, but you're just getting started. You shouldn't have to worry about not shocking yourself while you're 25ft up in a bucket truck for the first couple dozen times. You can always check voltage safely at the base of the pole, and then ring out the non-live wires to see if they're good up to the top of the pole.
Fortunately LEDs are replacing HID lighting. Every time i replace a magnetic ballast i feel good knowing that one day soon ill replace my last one!