Hello all,
Could you please help me with these questions:
1) Currently there are two 4000A 480V switchboard fed from two utility transformers. These two switchboards (both were designed same time from same manufacturer) share a N.O. breaker (same size as the two main breakers).
I think the intend is if one Tx was down, the N.O breaker will be closed so that two switchboards will be fed from the other Tx.
My question is what happens if the N.O. breaker become N.C. so that both switchboards will be fed from 2 Tx at the same time? In the event of fault current somewhere in this hypothetical system, both switchboards have enough AIC ratings to withstand the combined fault current created by the two Tx.
On the other hand, with the N.C. breaker, two swbds essentially become one bus. There's nothing wrong with two incoming power sources feeding one bus and its downstream loads. We see this setup with PV, micro turbine all the time.
Please advise me.
2) I have a SLD like this order: a MCC (no starter) - a feeder breaker - a VFD - a disconnect switch - a pump. My questions is: if the technician turns off the disc. sw (next to the pump) without locking/tagging out the feeder breaker, the upstream vfd doesn't know this and will continue to run without load. If this situation prolongs, would the vfd be damaged?
Usually I swap the order between a VFD and a disc. sw so that if the technician turn off the disc. sw, it will turn off the VFD also. But there are times when I have to put the vfd ahead of the disc. sw. due to various reasons.
I really appreciate your input. Thanks a lot.
Could you please help me with these questions:
1) Currently there are two 4000A 480V switchboard fed from two utility transformers. These two switchboards (both were designed same time from same manufacturer) share a N.O. breaker (same size as the two main breakers).
I think the intend is if one Tx was down, the N.O breaker will be closed so that two switchboards will be fed from the other Tx.
My question is what happens if the N.O. breaker become N.C. so that both switchboards will be fed from 2 Tx at the same time? In the event of fault current somewhere in this hypothetical system, both switchboards have enough AIC ratings to withstand the combined fault current created by the two Tx.
On the other hand, with the N.C. breaker, two swbds essentially become one bus. There's nothing wrong with two incoming power sources feeding one bus and its downstream loads. We see this setup with PV, micro turbine all the time.
Please advise me.
2) I have a SLD like this order: a MCC (no starter) - a feeder breaker - a VFD - a disconnect switch - a pump. My questions is: if the technician turns off the disc. sw (next to the pump) without locking/tagging out the feeder breaker, the upstream vfd doesn't know this and will continue to run without load. If this situation prolongs, would the vfd be damaged?
Usually I swap the order between a VFD and a disc. sw so that if the technician turn off the disc. sw, it will turn off the VFD also. But there are times when I have to put the vfd ahead of the disc. sw. due to various reasons.
I really appreciate your input. Thanks a lot.