Shackled Designer
Member
- Location
- Decatur, AL USA
Suppose I want to install a relatively small air conditioner on my industrial panel enclosure, and the AC unit is to be powered as a branch circuit from the mains feed into the panel. The air conditioner has a fairly low short circuit current rating of 5 kA, and the AC vendor has not bothered to test any fuse or circuit breaker combinations with the AC unit for a higher combo rating.
From a UL perspective, in order to increase the total panel SCCR, is it easier to simply put a transformer between the branch supply and the air conditioner (with no voltage change), or am I likely to be as successful improving the SCCR by simply putting a MCB on the branch circuit?
Other than testing the panel themselves, does UL provide any means for me to quantify panel SCCR with either method I have mentioned? I ask because whatever I do, at the end of the panel design, I have to document and label accurately the panel SCCR.
If the use of the transformer provides significantly higher SCCR as I expect, and/or a better solution for other reasons, then I have another question about the transformer sizing: must I size the transformer for the startup current of the air conditioner, or can I instead select a transformer based on the AC unit's running current?
The unit I have in mind has a startup current of about 12-13 amps, but its running current is not more than 2.5 amps. I imagine that the startup does not last for more than 2 to 4 seconds. Maybe another way of asking the transformer sizing question is whether a transformer's rating should reflect the expected inrush or some nominal margin above the expected constant load, say 125% of continuous current.
The NEC seems to provide direction on overcurrent protection for the transformer but, so far as I can discern, less instruction on transformer sizing with respect to the load itself.
Comments, questions, and criticisms are welcome.
Kind regards,
Shak
From a UL perspective, in order to increase the total panel SCCR, is it easier to simply put a transformer between the branch supply and the air conditioner (with no voltage change), or am I likely to be as successful improving the SCCR by simply putting a MCB on the branch circuit?
Other than testing the panel themselves, does UL provide any means for me to quantify panel SCCR with either method I have mentioned? I ask because whatever I do, at the end of the panel design, I have to document and label accurately the panel SCCR.
If the use of the transformer provides significantly higher SCCR as I expect, and/or a better solution for other reasons, then I have another question about the transformer sizing: must I size the transformer for the startup current of the air conditioner, or can I instead select a transformer based on the AC unit's running current?
The unit I have in mind has a startup current of about 12-13 amps, but its running current is not more than 2.5 amps. I imagine that the startup does not last for more than 2 to 4 seconds. Maybe another way of asking the transformer sizing question is whether a transformer's rating should reflect the expected inrush or some nominal margin above the expected constant load, say 125% of continuous current.
The NEC seems to provide direction on overcurrent protection for the transformer but, so far as I can discern, less instruction on transformer sizing with respect to the load itself.
Comments, questions, and criticisms are welcome.
Kind regards,
Shak