I don't have much experience with Class1 wiriring,
I'm going to wiring the dispenser pump motor for a new 500 gallon above ground storage tank that will be used for gasoline. There's already 3 tanks there that are "diked". This additional one will use the same circuit that already feeds the other pumps.
If I understand correctly, according to 514.3B, the shaded area in the drawing is C1D2?
The power that I'll tap off of is located at the existing middle tank but slightly outside the C1D2 zone (~4foot off the ground and about 4 foot away from the tank). Am I understanding this correctly? So when I tap off that power supply my raceway will be entering inter a C1D2 zone and I'll need a seal off before entering that zone?
When my raceway goes to the pump motor I'll need another seal off there also?
I plan to use 1/2" rigid as my raceway.
Also, the owner wants this tank operated with a key switch. Any recommendations about the "standard" or best way to accommodate this? I plan to call the supply house in the morning to see what they suggest. Should I do the key switch right at the tank dispenser or I can put the key switch where the power supply is that is just outside of the C1D2?
Thanks for suggestions and input!
I'm going to wiring the dispenser pump motor for a new 500 gallon above ground storage tank that will be used for gasoline. There's already 3 tanks there that are "diked". This additional one will use the same circuit that already feeds the other pumps.
If I understand correctly, according to 514.3B, the shaded area in the drawing is C1D2?
The power that I'll tap off of is located at the existing middle tank but slightly outside the C1D2 zone (~4foot off the ground and about 4 foot away from the tank). Am I understanding this correctly? So when I tap off that power supply my raceway will be entering inter a C1D2 zone and I'll need a seal off before entering that zone?
When my raceway goes to the pump motor I'll need another seal off there also?
I plan to use 1/2" rigid as my raceway.
Also, the owner wants this tank operated with a key switch. Any recommendations about the "standard" or best way to accommodate this? I plan to call the supply house in the morning to see what they suggest. Should I do the key switch right at the tank dispenser or I can put the key switch where the power supply is that is just outside of the C1D2?
Thanks for suggestions and input!