Questions around 1993 house square d main panel

Status
Not open for further replies.

tragichouse

New User
Location
Texas
Occupation
HomeOwner
I opened up my main service panel (Square D) to do a repair and have a couple of questions I'm hoping someone can answer. For extra information, my house was built in 1993 and this is the original service panel.

1. There are two small bus bars near the top left and top right of the panel. The left side has the grounds (from NM-B cables) and the right side has neutrals (also from NM-B cables).

a. Is the left one the ground bus bar and the right the neutral bus bar? Can the left side also have neutrals and the right side also have grounds?

b. I noticed some holes on the left side have doubled or tripled ground wires because there are no more available holes. What do I need to get or install in order to expand the number of slots?

c. I noticed the holes on the right side have neutral wires doubled up because there are no more available holes. What do I need to get or install in order to expand the number of slots?

2. I originally had a 4 AWG stranded copper insulated cable connected to the set screw right next to the service neutral lug at the top of the panel, which then connects to a grounding rod outside the garage in the ground. I was told I can replace this with a 6 AWG bare copper wire with no issues and is NEC compliant. Is this correct?

3. Pigtail inside main panel going to 20AMP breaker for washing machine circuitIt looks like the original installer or a past owner somehow damaged the black hot wire on one of the NM-B cables entering the panel. Because there wasn’t enough length left to reach the circuit breaker, they added a pigtail to extend it.


My understanding is that this may be against code and should be addressed. Can I simply move the circuit to another breaker position (which I have available) so the wire can reach without using the pigtail?

Also, do I need to be concerned about balancing the panel when moving the breaker? Is there any requirement for the left and right sides of the service panel to have some sort of balance in breaker amperage, or is that not really a thing?

I have attached pictures of the inside of my panel. It would also be awesome if someone could point out any other code violations i might need to get addressed as well.


 
Please try diychatroom.com

This site is designed for:

  • Electrical Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals
This NEC® Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.

Knowledge and the practical application of the National Electrical Code is an essential part of all electrical installations. If it's important for you to understand the National Electrical Code, then look no further.

To better help us serve you, please be sure to update your account details with your occupation field and location if you have not done so already. You can access your account details by clicking on your account name at the top right of the page when on the forums.
 
Status
Not open for further replies.
Top