Hi i have a couple of questions on a 4200 square foot church i'm helping out on. they're trying to save every penny they can. The electrical print shows lighting and plug layout and thats about it.
I wanted to install square d panels, they decided to got with homeline, to save money.
Question 1 the homeline panel AIR is 10k is this something i should be concerned with? square d AIR is 22k. this will be a new 400 amp service (ct can 2 200 amp panels) i don't know the size of the new transformer.
Question 2 panel location? the only good place to locate the panels is in a class room i couldn't find anything in the code book that said i couldn't put them there, but maybe i missed something? this church has no electrical or mechanical room.
Question 3 a/c feeders, there will be 2 4ton a/c units. is there a rule of thumb on what size wire to run for each unit or current per ton on these units. they want the power ran now and will add the a/c units in a couple of years.( heat is gas)
Question 4 current carrying conductor for 310-15 the neutral is not counted for convenience plugs ( no shared neutral),but is counted on flourescent lighting ( 120/240 3 wire system)
Question 5, where would you install the box ( high, low, middle) and what size wire would you run for a double oven. i have no idea what kind or brand of oven they will get, they just added it friday. any guesses?? it shouldn't require 2 boxes should it?
thanks for any help
I wanted to install square d panels, they decided to got with homeline, to save money.
Question 1 the homeline panel AIR is 10k is this something i should be concerned with? square d AIR is 22k. this will be a new 400 amp service (ct can 2 200 amp panels) i don't know the size of the new transformer.
Question 2 panel location? the only good place to locate the panels is in a class room i couldn't find anything in the code book that said i couldn't put them there, but maybe i missed something? this church has no electrical or mechanical room.
Question 3 a/c feeders, there will be 2 4ton a/c units. is there a rule of thumb on what size wire to run for each unit or current per ton on these units. they want the power ran now and will add the a/c units in a couple of years.( heat is gas)
Question 4 current carrying conductor for 310-15 the neutral is not counted for convenience plugs ( no shared neutral),but is counted on flourescent lighting ( 120/240 3 wire system)
Question 5, where would you install the box ( high, low, middle) and what size wire would you run for a double oven. i have no idea what kind or brand of oven they will get, they just added it friday. any guesses?? it shouldn't require 2 boxes should it?
thanks for any help