Questions for the forum:
Panel change out all EMT & Rigid into the original panel, panel is flush in wall.
No equipment grounds pulled in.
No way to verify where all the EMT goes, but some is for lighting and surely has some FMC in the run.
Circuits are all 15 and 20 Amp, now it would be a bit easier for me to use some short sections, less than 12" of metal flex to adapt the old raceways into the new panel is this legit code wise?
The issue is I can't prove the total amount of flex in the run is less than 6 feet.
The code section 250.118 is confusing.
Second question do I need to add a equipment ground bar in new panel?
The feeder is in rigid no wire type ground. I could add a bond bushing and short piece to a ground bar but the boss is cheap and would require a code reference.
Third issue is outside the building there is brand new a section of liquid tight flex in the middle of a run of conduit (40A breaker). It might even be non-metallic flex. If both ends of that run are attached to building steel and other raceways that are grounded is that or was that ever legal? Looks like someone tried to do a quick fix.
Thank you
Panel change out all EMT & Rigid into the original panel, panel is flush in wall.
No equipment grounds pulled in.
No way to verify where all the EMT goes, but some is for lighting and surely has some FMC in the run.
Circuits are all 15 and 20 Amp, now it would be a bit easier for me to use some short sections, less than 12" of metal flex to adapt the old raceways into the new panel is this legit code wise?
The issue is I can't prove the total amount of flex in the run is less than 6 feet.
The code section 250.118 is confusing.
Second question do I need to add a equipment ground bar in new panel?
The feeder is in rigid no wire type ground. I could add a bond bushing and short piece to a ground bar but the boss is cheap and would require a code reference.
Third issue is outside the building there is brand new a section of liquid tight flex in the middle of a run of conduit (40A breaker). It might even be non-metallic flex. If both ends of that run are attached to building steel and other raceways that are grounded is that or was that ever legal? Looks like someone tried to do a quick fix.
Thank you