Hi, hoping for a bit of help. Today at work, a fairly large new lathe that's been sitting unused for months suddenly became a crisis and my illustrious management team (the same geniuses that buy 208V equipment in a facility with 480V distribution) is now in a rush to fire it up by Friday.
Info sent from manufacturer and local rep is 208/220 3Ø 45KVA. The sum of all motors (I physically looked) is 32KVA. But nameplate is stamped 208/220 3Ø 65KVA. Made in Taiwan, of course, with, IMO, poor electrical documentation. Note - It is extremely doubtful the machine will ever run anywhere near full load current as it's overkill for the work being performed. That said...
A 480/208 45 KVA delta/wye xfmr has already been set by others, primary wired with 3x #6 thhn and #10 ground in 3/4" EMT and greenfield, fused at 50a. As there will be no secondary OCPD other than the lockable machine main disconnect/OCPD, I sized the secondary conductors for the full xfmr rating of 45KVA, 125amps at 208V (75°C), running 3x #1 thhn and a #6 ground in 1 1/4" EMT. There is no neutral connection at the machine itself. Does this seem correct?
My understanding is the EGC from the machine, the supply side ground, the xfmr frame/enclosure all connect at the same point/lug and be connected to X0 at the xfmr secondary via system bonding jumper. Correct?
All conductors on both primary and secondary to be run in EMT/greenfield and with ground wire as well. No concentric knockouts will be used, secondary is under 250V, so I don't believe grounding locknuts or grounding bushings are required. Correct?
Any help or comments on the above is really appreciated.
Thanks!
Info sent from manufacturer and local rep is 208/220 3Ø 45KVA. The sum of all motors (I physically looked) is 32KVA. But nameplate is stamped 208/220 3Ø 65KVA. Made in Taiwan, of course, with, IMO, poor electrical documentation. Note - It is extremely doubtful the machine will ever run anywhere near full load current as it's overkill for the work being performed. That said...
A 480/208 45 KVA delta/wye xfmr has already been set by others, primary wired with 3x #6 thhn and #10 ground in 3/4" EMT and greenfield, fused at 50a. As there will be no secondary OCPD other than the lockable machine main disconnect/OCPD, I sized the secondary conductors for the full xfmr rating of 45KVA, 125amps at 208V (75°C), running 3x #1 thhn and a #6 ground in 1 1/4" EMT. There is no neutral connection at the machine itself. Does this seem correct?
My understanding is the EGC from the machine, the supply side ground, the xfmr frame/enclosure all connect at the same point/lug and be connected to X0 at the xfmr secondary via system bonding jumper. Correct?
All conductors on both primary and secondary to be run in EMT/greenfield and with ground wire as well. No concentric knockouts will be used, secondary is under 250V, so I don't believe grounding locknuts or grounding bushings are required. Correct?
Any help or comments on the above is really appreciated.
Thanks!