jhm5016
Member
- Location
- Pennsylvania
I am tasked with designing a flameproof wire bushing to allow 25 wires to pass from a flameproof compartment to a non-flameproof compartment. Our certifier is using standard UL 1203 to evaluate this design for US certification. I have been told that the chemical compatibility test of UL 1203 (Cl. 33.3) will need to be performed on a bushing sample with the wires. I have found a few sealants that are advertised as suitable but I can not find any information on wire insulation types (e.g- PVC, ETFE, XLPE) that are known to pass this chemical test.
My search for UL 1203 compatible sealants and wires has created a lot of confusion. Perhaps nothing exemplifies my confusion better than the widely-available flameproof solid conduit fittings which use cement-based sealants. My research is suggesting that these cement-based sealants are not subject to chemical resistance testing. Furthermore, I do not see any specific limitations for wire types that are to be used with these flameproof conduit fittings. This would seem to suggest that chemical resistance is not an issue.
We have also spoken with a company that specializes in flameproof wire bushings and they have indicated that only their sealant was chemical tested and that the wires were never considered by their certification agency. This only adds to the confusion.
I am wondering now if our certifier is applying this test correctly. Things are not adding up. Has anyone here had experiences certifying a flameproof wire bushing? Any assistance with making sense of this chemical test would be greatly appreciated.
My search for UL 1203 compatible sealants and wires has created a lot of confusion. Perhaps nothing exemplifies my confusion better than the widely-available flameproof solid conduit fittings which use cement-based sealants. My research is suggesting that these cement-based sealants are not subject to chemical resistance testing. Furthermore, I do not see any specific limitations for wire types that are to be used with these flameproof conduit fittings. This would seem to suggest that chemical resistance is not an issue.
We have also spoken with a company that specializes in flameproof wire bushings and they have indicated that only their sealant was chemical tested and that the wires were never considered by their certification agency. This only adds to the confusion.
I am wondering now if our certifier is applying this test correctly. Things are not adding up. Has anyone here had experiences certifying a flameproof wire bushing? Any assistance with making sense of this chemical test would be greatly appreciated.