Hi All,
Here is the scenario: 2017 NEC, 208V, 3-phase, 4W, WYE-WYE, 35 degree C 2% high ambient temperature in ASHRAE, 3-current carrying conductors(L1,2 and 3) in the conduit. All lugs and breakers the conductors connected to are rated at 75 degree C. Continuous output current is 279A and we are using CU THWN-2 wire. We know the OCPD size should be 350A since it's the next size up of (279x1.25=348.75A). What is the minimum size of conductors? The AC run is very short so please don't consider voltage drop here. I got 500 kcmil but my colleague is saying 400 kcmil is fine? The 690.8(B) is telling me the conductor ampacity should be greater than (279x1.25=348.75A) and I looked up the 75 degree C column of 310.15(B)(16) due to the article 110.14 (C) (1) (b).
Thanks very much in advance!
Here is the scenario: 2017 NEC, 208V, 3-phase, 4W, WYE-WYE, 35 degree C 2% high ambient temperature in ASHRAE, 3-current carrying conductors(L1,2 and 3) in the conduit. All lugs and breakers the conductors connected to are rated at 75 degree C. Continuous output current is 279A and we are using CU THWN-2 wire. We know the OCPD size should be 350A since it's the next size up of (279x1.25=348.75A). What is the minimum size of conductors? The AC run is very short so please don't consider voltage drop here. I got 500 kcmil but my colleague is saying 400 kcmil is fine? The 690.8(B) is telling me the conductor ampacity should be greater than (279x1.25=348.75A) and I looked up the 75 degree C column of 310.15(B)(16) due to the article 110.14 (C) (1) (b).
Thanks very much in advance!