I work in the Mining Industry and the company that I worked for was in the design phase of building a new secondary stone plant. We used AggFlow software to help determine motor HP. I determined what size of pad mount transformer I needed to run the equipment and we bought a used transformer for this project. Since then, the company sold out to a competitor and they have decided to add even more equipment. I now have the issue of not having enough transformer to do the job. Due to the cost of buying another transformer, the new company wanted me to look into the option of having our local utility supply me with secondary power. So this is where my question comes from.
The way that I have determined what size of transformer that I need for these types of projects is to use the FLA from the NEC for each motor minus the largest motor FLA and find out what my 3 phase KVA would be. Then I would add 3 times the largest motor HP. I understand that if I used some type of a controlled start, whether it is a soft start or vfd on the largest motor I may not need 3 times, but this usually adds a little extra to the system and helps prevent voltage drop on startup. In this case the largest motor is 300 HP and I will be using a current ramp soft start. I have seen times where people use the exact same idea, but they do not find 3 phase KVA. This always made me a little weary, but if the system doesn't start loaded then they are probably alright. My local utility only wants to supply me with 1KVA per HP and as a matter of fact that number produced an odd size transformer so they want to actually step down a little from that since the motors don't run fully loaded. My calculation came up with 2400 KVA for startup so I say that I need a 2500 KVA transformer and the local utility wants to provide me with 1500 KVA for 1609 HP. Who is right? Am I way over or are they way under?
Any insight would be greatly appreciated.
thanks,
The way that I have determined what size of transformer that I need for these types of projects is to use the FLA from the NEC for each motor minus the largest motor FLA and find out what my 3 phase KVA would be. Then I would add 3 times the largest motor HP. I understand that if I used some type of a controlled start, whether it is a soft start or vfd on the largest motor I may not need 3 times, but this usually adds a little extra to the system and helps prevent voltage drop on startup. In this case the largest motor is 300 HP and I will be using a current ramp soft start. I have seen times where people use the exact same idea, but they do not find 3 phase KVA. This always made me a little weary, but if the system doesn't start loaded then they are probably alright. My local utility only wants to supply me with 1KVA per HP and as a matter of fact that number produced an odd size transformer so they want to actually step down a little from that since the motors don't run fully loaded. My calculation came up with 2400 KVA for startup so I say that I need a 2500 KVA transformer and the local utility wants to provide me with 1500 KVA for 1609 HP. Who is right? Am I way over or are they way under?
Any insight would be greatly appreciated.
thanks,