Office gets a call yesterday about multiple pieces of equipment not working at large country club served by Florida's largest provider. The owner of our company goes there and gets odd voltage readings and determines it a POCO issue.
I get sent there this morning for same issues and find I have lost high leg of a 240/120 open delta. I report my findings to clubs general manager and he states POCO was there 5pm yesterday and said all is well. I tell them to call POCO again.
I go outside and poke around, all looks OK in POCO vault, so go a couple hundred feet out to pole. Got 2 primaries with 2 cut-outs on the pole that go underground to vault. Both cut-outs are closed but there is a small piece of wire hanging out the bottom of one fuse.
I'm out there getting pics of fuse and pole # when GM comes out and says POCO doesn't believe me. We go back into his office so he can send them the pics I took. There he shows me the E-mail of the POCO linemans report from previous night. The report shows L1,L2,L3 to N voltages all right around 120V.
Here's a clue lineman, with all breakers closed on a partial power call you just might want to check L-L voltages also.
3 hours later POCO replaces fuse and I'm back on line.
(sorry, not such a short story after all)
I get sent there this morning for same issues and find I have lost high leg of a 240/120 open delta. I report my findings to clubs general manager and he states POCO was there 5pm yesterday and said all is well. I tell them to call POCO again.
I go outside and poke around, all looks OK in POCO vault, so go a couple hundred feet out to pole. Got 2 primaries with 2 cut-outs on the pole that go underground to vault. Both cut-outs are closed but there is a small piece of wire hanging out the bottom of one fuse.
I'm out there getting pics of fuse and pole # when GM comes out and says POCO doesn't believe me. We go back into his office so he can send them the pics I took. There he shows me the E-mail of the POCO linemans report from previous night. The report shows L1,L2,L3 to N voltages all right around 120V.
Here's a clue lineman, with all breakers closed on a partial power call you just might want to check L-L voltages also.
3 hours later POCO replaces fuse and I'm back on line.