Quick question about grounding and bonding
The electron man
Nyc
The reason we don't Bond at the sub-panel
Is Because the neutrals can leak voltage to the grounds plus in case of a ground fualt ,we don't want a parallel path back to the source if I'm correct
So at the main panel why aren't we worried that the neutrals will leak voltage to the grounds?
We don't want a compromised neutral to accidentally energize conductive parts expected to be grounded.
At the service, the system neutral is the premises zero-voltage reference to which the EGC is connected.
Because in normal, non-fault conditions, you want zero current flow in the grounding conductors. That way they won't have a potential difference to grounded objects, they're always safe to touch, and safe to bond conductive items to.