Quick question conduit size

Status
Not open for further replies.
Twoskinsoneman said:
I may be crazy but I thought there was a NEC article that generally limited conduit sizes to 1/2" and larger...

That would depend on the conduit type in particular...some go as low as 3/8" (356.20)
 
infinity said:
Since he said "branch circuits" I would guess that it's 1/2".

I dunno....I *could* jam 8 #14 THHN's in a 3/8" LFNC...not that I would....but I could according to TC5....that'd be branch circuitS :grin:
 
celtic said:
I dunno....I *could* jam 8 #14 THHN's in a 3/8" LFNC...not that I would....but I could according to TC5....that'd be branch circuitS :grin:


That likely would be a violation of 356.20(A).
 
Luminaries and motors...with limitations as Infinity described.

Check the 3xx.20 sections in regards to flexible raceways.


If you can be a bit more specific...we can be a bit more specific.
 
Without going through the NEC, I am confident in saying off the top of my head that the following raceways are not permitted in sizes smaller than metric designator 16, trade size 1/2: Thinwall, IMC, GRC, Greenfield, Sealtite, RNC, HDPE, and Smurf. I'm sure LFNC and any others that aren't coming to mind probably follow this rule as well. The only way you will be using < (1/2") knockouts is with a cable assembly of some sort. I hope that was the question that was being asked. ;) :smile: ;)
 
Pi.
Check the 3xx.20 sections in regards to flexible raceways....while the raceway is 3/8", the connector may very well be 1/2" at the threads.
 
celtic said:
Pi.
Check the 3xx.20 sections in regards to flexible raceways....while the raceway is 3/8", the connector may very well be 1/2" at the threads.


I think you mean that the other way around, but either way, you snagged me. The raceway (barring fixture whips, which I failed to note) may not go below t/s (1/2), though it very well could have a 3/8 connector, true enough.
 