I checked out a job today and I need to wire up a 16kw Generator for the homeowner.
The run is 125' total including the wire needed outside to the generator if I go diagonal through the web joists in his basement. The breaker on the generator is 65A and the transfer switch/panel calls for a 70A breaker.
Can I run a 4-4-4-6 AL SER for the main power, or does it need to be a 2-2-2-4 AL SER?
He wanted all copper conductors and it would cost him a fortune if I had to run pipe and THHN the whole way because the run would be longer.
If I end up drunning SER would I be able to put a junction box inside, strip the SER back and run it in pipe from the J-Box to the Generator(About 12 feet)?
Also What would you guys suggest for running the four control wires?
Small FMC through the joists to the J-box?
Please excuse my ignorance, I just want to make sure I'm goign to do this right and I'm rusty on residential.
Thanks!
-Ian
The run is 125' total including the wire needed outside to the generator if I go diagonal through the web joists in his basement. The breaker on the generator is 65A and the transfer switch/panel calls for a 70A breaker.
Can I run a 4-4-4-6 AL SER for the main power, or does it need to be a 2-2-2-4 AL SER?
He wanted all copper conductors and it would cost him a fortune if I had to run pipe and THHN the whole way because the run would be longer.
If I end up drunning SER would I be able to put a junction box inside, strip the SER back and run it in pipe from the J-Box to the Generator(About 12 feet)?
Also What would you guys suggest for running the four control wires?
Small FMC through the joists to the J-box?
Please excuse my ignorance, I just want to make sure I'm goign to do this right and I'm rusty on residential.
Thanks!
-Ian