Hi. It's been a while since I've done a voltage drop calculation. I tried using a couple of online calculators but they are giving different answers and not showing how they do the math. I want to make sure I know how to do it right.
Here's the situation: 480V/3ph 75kW load (=90A), 150' from the panel.
I also looked at this post: http://forums.mikeholt.com/showthread.php?t=83435&page=3&p=649546#post649546
But it uses DC resistance values from Table 8. Not clear why you wouldn't use the AC values from Table 9. I guess they're usually very close.
For #6 conductors:
Vd = 1.73 * 0.49/1000 * 90 * 150' = 11.44V dropped
480-11.44 = 468.6V
1- 468.6/480 = 2.5% voltage drop. This is within the 3% generally accepted branch circuit limit so I should be good. Does this make sense? Thanks for the help!
PS- This agrees with the calculator here, but not the second one here.