riverj said:once you enter a roof top unit do you have to continue to run a raceway to the back of a disconect or can you run them without a raceway inside the R.T.U.
don_resqcapt19 said:In my opinion you need a raceway until you get to the wiring compartment.
My defintion of the "wiring compartment" is the enclosure within the equipment that contains the contactor and other control elements.I agree but with many units the minute you enter the unit from below you are in the 'wiring compartment'
We got problems. I plan on doing this on 2 of the 8 RTU's at the club. If your dept. tags these installs, what do you think the factory KO's under the unit are for?Watt-Me worry? said:Yeah, I'd turn it down based on the definition of Disconnecting Means. Further, I couldn't think of any code that would allow an RTU to be used as a raceway. The intent is to make the unit safe for a serviceman.
iwire said:I agree but with many units the minute you enter the unit from below you are in the 'wiring compartment'