J J.A.M. Member Feb 6, 2008 #1 Do Nuteral Wires Count in pipe fill ? If so were is it stated in the NEC?
roger Moderator Staff member Location Fl Occupation Retired Electrician Feb 6, 2008 #2 All conductors count in conduit or tubing fill even the EGC, see chapter 9, note 3 to the Table notes. Are you thinking about the neutral being counted for derating purposes? Roger
All conductors count in conduit or tubing fill even the EGC, see chapter 9, note 3 to the Table notes. Are you thinking about the neutral being counted for derating purposes? Roger
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 6, 2008 #3 Think of the words that you mentioned "pipe fill". If it fills the pipe it counts for conduit fill. This would included ungrounded, grounded and grounding conductors.
Think of the words that you mentioned "pipe fill". If it fills the pipe it counts for conduit fill. This would included ungrounded, grounded and grounding conductors.