benaround said:I can't find it. I think the OP is asking where in the NEC does it tell you
where to look, or what table to use, for the conductor that loops from the
bonding bushing on the end of each of 3 metal service entrance raceways,
to the EG bus. I'm seeing 3 RMC's coming into a open bottom SES ea. has
a bond bushing, I can't find the words in the NEC for this situation .as to
how to size this bonding wire.
I always use 250.66, but this is not an electrode??
eprice said:The code reference is 250.112(C).