Where is it stated in the NEC the entire raceway system shall be installed prior to installing cable?
300.18 Raceway Installations. (A) Complete Runs. Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, junction, or splicing points prior to the installation of conductors.
Is it really that bad? It doesn't say every last stick and box for the entire job scope has to be installed before pulling wire, just between point "A" and point "B", and you get to pick. I would think you wouldn't want someone running a 1" RMC over some wire and then screwing it into a hub or EL. It's bad practice, for one, and you could abrade the wire, for another.That one is on my (long) list of code sections that should be nixed. Let's let the electricians in the field decide the best way to do something thank you.
when would it ever matter? the only thing this prohibits is putting the conductors inside the conduit before installing the conduit.That one is on my (long) list of code sections that should be nixed. Let's let the electricians in the field decide the best way to do something thank you.
So, if you have to do a panel replacement, you must pull all wires back to the first junction box, replace the panel and then pull all the wires back in. Right! That code stinks. It is on the top of my list as well. Also, flex is a raceway. When was the last time you pulled wire through the conduit system and the 90 degree flex connector. If you pulled and then connected to the connector, you violated code.Is it really that bad? It doesn't say every last stick and box for the entire job scope has to be installed before pulling wire, just between point "A" and point "B", and you get to pick. I would think you wouldn't want someone running a 1" RMC over some wire and then screwing it into a hub or EL. It's bad practice, for one, and you could abrade the wire, for another.
This is what Mike has said at his seminars when someone complains. However, I have been known to push wires thru a section of flex or a slide the LB over.“Code is code
We don’t like the rules we don’t agree with
They are ok for someone else
But not if they cost us time and money”
Mike Holt
As an inspector, I didn't have the time to babysit a job to make sure the installer complied with that code.
Or several other codes for that matter.
Ron
I can see your point. And it's possible, now that I think about it, that I may have slid a compression elbow or two over the conductors before connecting to the box or conduit.Ok , 3.5" 45 degree sealtite connector. Sleeve over conductors or pull thru??