A Alwayslearningelec Senior Member Location NJ Occupation Estimator Mar 17, 2025 #1 If you saw this drawing note would you always interpret the raceways to be a "Wiremold" type of raceway or EMT etc.?
If you saw this drawing note would you always interpret the raceways to be a "Wiremold" type of raceway or EMT etc.?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 17, 2025 #2 I would assume Wiremold. They specifically mentioned the other portion which is EMT.
roger Moderator Staff member Location Fl Occupation Retired Electrician Mar 17, 2025 #3 Not to mention that "surface raceway" is an NEC term, see articles 386 and 388
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Mar 17, 2025 #4 roger said: Not to mention that "surface raceway" is an NEC term, see articles 386 and 388 Click to expand... Surprised to see that they actually used the code term instead of Wiremold.