I have a question regarding raceways installed in cabinets. Does the raceway have to be securely installed with a connector?
3" PVC penetrates the Concrete slab into a 3 phase 800 Amp Transfer switch. The bottom support braces keep the 3" PVC penetrations 10" to 12" off the slab. Three and a half inch holes are punched and PVC Bushings are used bringing the PVC stubs four inches into the cabinet.
Article 312.5 (A) States Openings through which conductors enter shall be adequately closed.
300.5 (G) Mentions raceway seal but I don't believe this to apply to my question.
300.10 Proclaims; Unless specifically permitted elsewhere in this Code, raceways and cable assemblies shall be mechanically secured to boxes, fitting,cabinets and other enclosures.
Is this the correct installation; The three inch PVC is changed to rigid stubs, proper holes are punched, and bonding bushings are used.
Any feedback is always appreciated.
Justin W.
3" PVC penetrates the Concrete slab into a 3 phase 800 Amp Transfer switch. The bottom support braces keep the 3" PVC penetrations 10" to 12" off the slab. Three and a half inch holes are punched and PVC Bushings are used bringing the PVC stubs four inches into the cabinet.
Article 312.5 (A) States Openings through which conductors enter shall be adequately closed.
300.5 (G) Mentions raceway seal but I don't believe this to apply to my question.
300.10 Proclaims; Unless specifically permitted elsewhere in this Code, raceways and cable assemblies shall be mechanically secured to boxes, fitting,cabinets and other enclosures.
Is this the correct installation; The three inch PVC is changed to rigid stubs, proper holes are punched, and bonding bushings are used.
Any feedback is always appreciated.
Justin W.