diamondrobot
New member
In our industrial setting, we rack out our 480v breakers to perform lockout / tagout. The question has came up about being safer to not rack out the breaker, due to flash protection zone (NFPA 70). Our stand was that the locking tab did not provide a true lock out point, but acted as a mechanical interlock. A quote from our electrical specialist.... has guideline 1910.333 b 2 ii B which states "... circuits and equipment to be worked on shall be disconnected from all electric energy sources. Control circuit devices, such as push buttons, selector switches, and interlocks, may not be used as the sole means for de-energizing circuits or equipment. Interlocks for electric equipment may not be used as a substitute for lockout and tagging procedures." Many new questions with the NFPA 70 standard.