mkgrady
Senior Member
- Location
- Massachusetts
A friend of mine is having under floor electric radiant heat installed by a tile installer. The installer layed out the wire on the floor. My friend asked for the results of the Megohm test. The value must be at least 1000 megohms at a test voltage of 1,000. The tile installer responded that he just uses a multi meter to confirm the ohm value of the heater. Meaning he does not bother with the Megohm test thereby voiding the warranty. Shame on the tile guy for Allowing this step to be skipped.
Of course the test should be done by an electrician so my friend called me to conduct the test. I performed the test using my extech 380260 Megohm meter. Both heater cables failed the test. One cable read 460 megohms and the other read 160. The tile guy then rips out the newly installed heater cable and heads to his supplier to complain that the cable is defective. He returns with two new cables and they also fail the test.
The next day the tile installer shows up with a borrowed fluke Megohm meter and this time the cables pass the test. Each cable tested out at 2,200 megohms.
The likely conclusion is that my meter is defective but how can that be determined?
Of course the test should be done by an electrician so my friend called me to conduct the test. I performed the test using my extech 380260 Megohm meter. Both heater cables failed the test. One cable read 460 megohms and the other read 160. The tile guy then rips out the newly installed heater cable and heads to his supplier to complain that the cable is defective. He returns with two new cables and they also fail the test.
The next day the tile installer shows up with a borrowed fluke Megohm meter and this time the cables pass the test. Each cable tested out at 2,200 megohms.
The likely conclusion is that my meter is defective but how can that be determined?