Re: Radio Antenna Grounding:
Hi guys, first sorry about the quote-without-material posting above, slipped there...
Most of the questions raised were answered in some part, but I can help with the ground requirements for radios...
All modern radio equipment must have their metal cases bonded individually to a single point ground for the radio room. This single point ground is of course bonded to the main structure AC entrance ground as well as antenna mast grounding systems.
An antique radio (assume non-metallic case and 2-prong plug, the worst possibilities) of which the poster speaks is a rather dangerous piece of equipment. They should never, ever be connected to external antennas when there is any chance of approaching thunderstorms!
One member raised the question "doesn't it make a ground loop when coax is grounded at the radio (thru the AC fault-ground), and the antenna is grounded outside"? Yes it does make an unavoidable loop. But the entire grounding system is bonded so that's not a loop that causes any harm. All antenna coax feedlines must be shield-grounded at several locations, including the station entrance and of course again at the radio by coax connector design.
Never, ever, may a separate ground connection (such as unbonded water pipe or unbonded separate gronding electrode) be used for a radio connected to external antennas.
I have never heard any person concerned with the possiblity that an electrical fault somewhere else might also harm their radio IF the neutral or ground was ALSO open somewhere.
Jack Painter
Virginia Beach