How does the NEC address grounding a radio antenna?
810.21 I'm guessing you already read this and there is more to the question.:smile:tryinghard said:How does the NEC address grounding a radio antenna?
chris kennedy said:810.21 I'm guessing you already read this and there is more to the question.:smile:
tryinghard said:No more intentionally I just posted while opening my book. I have an antenna portion to one of my projects and I want to verify its grounding.
I wonder if 820 plays a role because at a glance it looks like these may ground differently? I may need to ask the technician that’s supplying the antenna what type it is?
oceanaradio said:That's a good start. Because this question often comes up, it might be easier to think in these terms:
An "Antenna" is never grounded. It's metallic *base* and the mast (if provided) is bonded to an equipotential grounding system...
tryinghard said:How does the NEC address grounding a radio antenna?
K8MHZ said:Lot's to learn here:
www.polyphaser.com
NEC requirements in chapter 8 are the barest of minimums. Antennas may require 3 different grounds, RF ground, lightning protection and AC mains safety. Whatever is sought, the ground system of an antenna must be connected to the AC mains system.
tryinghard said:Thanks, the ground I'm talking about is to the existing electrode system and if I did install another electrode it would become a part of this ground system as well.
A technician will be responsible for the antenna furnish & installation, I?m just making sure it?s grounded to NEC.
All you have to worry about is 810.21 and running the bonding conductor from the mast to the nearest GES or water pipe.tryinghard said:Jack,
I'm just grounding the mast, lightning reasons, wouldn't 810.21 apply?
dereckbc said:All you have to worry about is 810.21 and running the bonding conductor from the mast to the nearest GES or water pipe.
That is why you have to read, including the references. Since the GES is likely outside and the closest point kind of makes it a NO-BRAINER :grin:tryinghard said:I agree but only if the water pipe is an electrode.
Many places the water pipe is simply only a water pipe that is bonded as per 250.104 and not an electrode as per 250.52.
dereckbc said:That is why you have to read, including the references. Since the GES is likely outside and the closest point kind of makes it a NO-BRAINER :grin:
dereckbc said:That is why you have to read, including the references. Since the GES is likely outside and the closest point kind of makes it a NO-BRAINER :grin:
oceanaradio said:A coaxial surge protector (some call these arrestors) must be installed to protect the sensitive receiver-components of all radios with external antennas.
BarryO said:This may be a good idea, but is not required by Article 820.