Rain Gutters conducting Have 68 volts to ground

Status
Not open for further replies.

arnettda

Senior Member
I went on a service call where people were getting shocked when touching the gutters. I put my volt meter between the gutter and a rod I stuck in the ground and found 68 volts to ground. I traced it to a wire that I believe must have gotten a nail in it from the metal lathe they used to but stone on the side of the building. I fished in a new wire but still have 1.5 volts to ground. With the circuit turned off I have .40 volts to ground. The home run comes into a light fixture and splits two ways. One wire feeds the lighting and another wire runs down to the outlets. When I hook up the lighting wire I get just under 1 volt to ground. And then when I hook up the wire for the outlets I get the full 1.5 volts to ground.
Should I be concerned with this 1.5 volts to ground? No where else on the house can I get a voltage reading to ground.( Meter socket, AC units other gutters etc.)
Only the breaker that feeds this area causes the .4 volts to ground go away. So I do not believe some other circuit is causing the problem. And the lighting circuit that cause it to go from .4 volts to just under 1 volt is the brand new wire I ran down to the switch.
Any thoughts would be appreciated. I really do not want this to become 68 volts again down the road.
 
The fact that any circuit lights up the gutter and goes dead when a breaker is off tells me you haven't located every misplaced nail. It's even possible your new cable was nicked by a nail point protruding into a drilled hole through a stud.
 
If you are measuring with a high impedance meter, it’s likely that the small voltages you are reading are simply phantom readings due to capacitive coupling.
 
The fact that any circuit lights up the gutter and goes dead when a breaker is off tells me you haven't located every misplaced nail. It's even possible your new cable was nicked by a nail point protruding into a drilled hole through a stud.

My new wire should not be the problem. It is in the garage and I ran a surface conduit from light down the wall and sleeved a 12/3 nm in the conduit and went right into the switch inside the house. Could not run conduit all the way because the switch was offset about a foot. Used a bushing on the conduit and cut a hole on the inside so I could fish the wire.
 
I would kind of expect to read some small voltage from almost any ungrounded metal structure to ground when using a high impedance meter.

Or grounded. I get 1.7 volts with a high impedance meter from my bonded water pipe to an outdoor faucet to ground about 3 feet away. The voltage drops as I get closer to the pipe, which is buried in the ground.
 
True, but the fact that there are direct changes in these readings when breakers related to the original problem are cycled is troubling.

I disagree that it’s troubling. Energizing and deenergizing a circuit can definitely have an influence on capacitively coupled phantom voltages.
 
I disagree that it’s troubling. Energizing and deenergizing a circuit can definitely have an influence on capacitively coupled phantom voltages.
It's troubling if we don't know for certain that the voltage is caused by capacitance. A continuity test between the gutter and the circuit in question could help in this regard.
 
It's troubling if we don't know for certain that the voltage is caused by capacitance. A continuity test between the gutter and the circuit in question could help in this regard.

I would check the voltage with a low impedance meter. I’m betting it reads zero V.
 
what is the Ohm reading gutter to rod?
or put a wire between and measure current

if you are not reading it on other gutters and when you kill the cb it goes away imo you have a nick somewhere
on the meters, etc I would expect 0 since solidly bonded
 