i need some wise man's advice out there on these two mess-ups....
Brought an inspector to see our job yesterday, he did not like all the compression couplings/connectors i run because they were not 'RAIN TIGHT'.
i have known this code for a while but since no other inspectors had said anything about it for years it had slipped away from me... now this guy is serious about this (314.15./358.42). I get that. it is my fault. i am trying to fix it now.
my question is that if i used XHHW-2 wires (for wet location), would that be ok without having to fix the fittings to 'rain tight' the raceway?. I m not sure... maybe not.
second, he mentioned about heat shrink around the fittings to 'rain tight' so that we don't have to pull all wires out and replace them all... seems it is still time consuming as well. Or if you have any better way to solve this mess.
other issue i had with him was 3"LBs. i put 'regular LBs' and he asked me what the wire size gonna be, i said '500kcmil'... then he said i have to use larger LBs so that the wires run is not 'damaged with too much bent (314.28/314.28A.3). i looked into it and they are not cheap. and out of stock in many places. Should i replace with nema 3R junction box? i am running two parallel run of 3". any advice on this?
Thank you guys for your feedback. appreciate it as always.
Brought an inspector to see our job yesterday, he did not like all the compression couplings/connectors i run because they were not 'RAIN TIGHT'.
i have known this code for a while but since no other inspectors had said anything about it for years it had slipped away from me... now this guy is serious about this (314.15./358.42). I get that. it is my fault. i am trying to fix it now.
my question is that if i used XHHW-2 wires (for wet location), would that be ok without having to fix the fittings to 'rain tight' the raceway?. I m not sure... maybe not.
second, he mentioned about heat shrink around the fittings to 'rain tight' so that we don't have to pull all wires out and replace them all... seems it is still time consuming as well. Or if you have any better way to solve this mess.
other issue i had with him was 3"LBs. i put 'regular LBs' and he asked me what the wire size gonna be, i said '500kcmil'... then he said i have to use larger LBs so that the wires run is not 'damaged with too much bent (314.28/314.28A.3). i looked into it and they are not cheap. and out of stock in many places. Should i replace with nema 3R junction box? i am running two parallel run of 3". any advice on this?
Thank you guys for your feedback. appreciate it as always.