Anyone familiar with grounding/bonding raised floor systems in a server room? From 645.15, I take it that all posts shall be bonded to an equipment grounding conductor, and I have been reading IEEE 1100-2005 regarding Single Reference Grids. I'm trying to understand if the SRG is the flat wire grid, the grounding/bonding conductor net, or if 645.15 requires the SRG be bonded and a grounding grid be installed. Thoughts? Anyone with experience?
Also, I read that for 3000 sqft of raised floor, a #4/0 bare grounding net is required... where is that information found (no reference in article)? In a different article, I also read that the resistance should be 4 ohms or less.
Articles referenced.
Also, I read that for 3000 sqft of raised floor, a #4/0 bare grounding net is required... where is that information found (no reference in article)? In a different article, I also read that the resistance should be 4 ohms or less.
Articles referenced.
Raised Access Floor Grounding Requirements, Solutions, Maintenance for Data Center and Computer Room
In this article, Huiya - Professional Access Floor Supplier, will discuss the grounding requirements and solutions for the raised floor of the computer room and data center with you in detail.
www.accessfloorstore.com