Raised Floor Distribution System

Merry Christmas
Status
Not open for further replies.

jimatwork

Member
Would a raised floor system in a office building fall under Article 604 Manufactured Wiring Systems ? The system for example would be the Hubbell Connexion Zone Distribution System. The zone distribution boxes are hard wired from electrical panel to zone box i know for what ever wiring method you used it would have to strapped accordingly. Do the extender cables (like reloc) that go to floor boxes installed in raised floor have to be straped?
 
And to answer the second part of your question that I missed:

Pursuant to 604.6 the cables will have to be secured as per the respective sections:

AC - 320.30
MC - 330.30
LFMC - 350.30
 
Thanks for your reply I have been doing a little more research and it looks it definitely falls under Art.604 Which would have to be supported as 604.6(E)
Which brings you to Art. 333.30 B
 