hbendillo
Senior Member
- Location
- South carolina
I've been doing a lot of research about when and how extensive the grounding of a raised floor needs to be. Related to that is the necessity of a Signal Reference Grid under a raised access floor. I think the SRG is largely unnecessary these days but there are still some applications where I use them or am directed to use them.
Anyway, my question is about raised flooring systems that don't used bolted stringers just isolated pedestals on which the floor is installed. Most of these flooring systems use floor tiles that metal on the bottom side and in affect when all floor tiles are installed are bonded together. But even if there weren't, I am not sure that is a necessity. But I am not getting a clear picture on the issue.
Well I am involved in a job where the raised floor system was changed from a bolted stringer type to a non-stringer type. The electrical contractor has issued a change order to install a ground system whereby each pedestal is grounded. Is that really necessary here?
Application: Office building with a technical support center that basically has open office areas and rooms with computer work stations. They also have flat panel video displays throughout. The main servers for the data delivery are installed in another area of the building.
I'd like to hear some opinions on whether we need to ground every pedestal or general comments about raised floor grounding for this application.
Thanks.
Anyway, my question is about raised flooring systems that don't used bolted stringers just isolated pedestals on which the floor is installed. Most of these flooring systems use floor tiles that metal on the bottom side and in affect when all floor tiles are installed are bonded together. But even if there weren't, I am not sure that is a necessity. But I am not getting a clear picture on the issue.
Well I am involved in a job where the raised floor system was changed from a bolted stringer type to a non-stringer type. The electrical contractor has issued a change order to install a ground system whereby each pedestal is grounded. Is that really necessary here?
Application: Office building with a technical support center that basically has open office areas and rooms with computer work stations. They also have flat panel video displays throughout. The main servers for the data delivery are installed in another area of the building.
I'd like to hear some opinions on whether we need to ground every pedestal or general comments about raised floor grounding for this application.
Thanks.