desllc04
Member
- Location
- Gloucester, Virginia
- Occupation
- Electrician
In reviewing the code articles in 250-140 and 250-142, and the requirements for upgrading the feeder conductors, (recepts and pigtail) from the now load panel to those appliances once an automatic transfer switch with a service disconnecting mean is installed. Because of the risk of unwanted current through the appliance to another grounded item,(sink or countertop appliance) the old uninsulated conductor in the SE cable is not permitted to serve as the grounded conductor, (neutral).
Thoughts?
Thoughts?