superdave02 Member Location South East Occupation Electrical Consultant May 2, 2025 #1 I have (10) 13kw ranges going into a vocational school. Do I add 5% to 25kw or 50%?? Table 220.55 Column C 2023 national electrical code
I have (10) 13kw ranges going into a vocational school. Do I add 5% to 25kw or 50%?? Table 220.55 Column C 2023 national electrical code
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) May 2, 2025 #2 5%
Jaybone812 Senior Member Location South shore. Massachusetts-2023 NEC Occupation Commercial & Residential Electrician May 2, 2025 #3 superdave02 said: I have (10) 13kw ranges going into a vocational school. Do I add 5% to 25kw or 50%?? Table 220.55 Column C 2023 national electrical code Click to expand... 5% your service load for the 10- 13 kw ranges is 26 1/4KW
superdave02 said: I have (10) 13kw ranges going into a vocational school. Do I add 5% to 25kw or 50%?? Table 220.55 Column C 2023 national electrical code Click to expand... 5% your service load for the 10- 13 kw ranges is 26 1/4KW
superdave02 Member Location South East Occupation Electrical Consultant May 2, 2025 #4 Thank you men!