I am studying for a test and I am supposed to do a feeder calculation for ranges.
Can anybody give me the rule for the notes 1 and 2 for table 220.19.
The question is at the point where you increase 5 percent for each additional kilowatt of rating or major fraction thereof by which the rating of individual ranges exceeds 12 kw.
What is major fraction? Does that mean anything over 12? I have a questions that calls for:
12- 12.8 KW ranges
12- 12.5 KW ranges
24- 11.6 KW ranges
I come up with a number of 12.325
Is that a major fraction thereof? 12.325 is not over 12.5 so I don?t know if I should give the 5% addition or not.
The test questions I have are designed to be tough I think, so I am finding all kinds of little troubles with my answers!
If anybody is curious the question is this:
What is the feeder demand for 12 ? 12.8KW household ranges, 12 ? 12.5KW ranges and 24 ? 11.6KW ranges if connected to a three-phase service? The answer is 45-50KW and is supposed to come right from the table.
I keep coming up with 33.75 without the 5% or 35.4375 with the 5%
Is there something I might be missing with the wording of household range and then just ranges? Oh, and everything I have done I have never done a 3 phase calculation until the end. And that was to find the amperage after the sums of all the loads had been calculated.
Can anybody give me the rule for the notes 1 and 2 for table 220.19.
The question is at the point where you increase 5 percent for each additional kilowatt of rating or major fraction thereof by which the rating of individual ranges exceeds 12 kw.
What is major fraction? Does that mean anything over 12? I have a questions that calls for:
12- 12.8 KW ranges
12- 12.5 KW ranges
24- 11.6 KW ranges
I come up with a number of 12.325
Is that a major fraction thereof? 12.325 is not over 12.5 so I don?t know if I should give the 5% addition or not.
The test questions I have are designed to be tough I think, so I am finding all kinds of little troubles with my answers!
If anybody is curious the question is this:
What is the feeder demand for 12 ? 12.8KW household ranges, 12 ? 12.5KW ranges and 24 ? 11.6KW ranges if connected to a three-phase service? The answer is 45-50KW and is supposed to come right from the table.
I keep coming up with 33.75 without the 5% or 35.4375 with the 5%
Is there something I might be missing with the wording of household range and then just ranges? Oh, and everything I have done I have never done a 3 phase calculation until the end. And that was to find the amperage after the sums of all the loads had been calculated.