Re: range calculations
Jim, just so you know, I'm not trying to give you a hard time.
Note 1 of table 220.19 says the maximum demand will be increased 5% for each additional kilowat of rating or major fraction thereof by which the rating of the individual ranges exceeds 12 KW. With this wording, the .4 being less than a major fraction could be dropped.
With this being the case, column C gives you the KW rating, not a percentage, so you would read across the quantity of 5 ranges line and see 20 KW as the answer.
Roger